Subject: Re: regarding MOV
-
Date: 09/17/03 at 8:10 AM
Posted by: Mahendran
E-mail: mail2mahendran[AT55]yahoo.com (replace [AT55] with @ to reply)
Message Posted:
-
In Reply to: Re: regarding MOV posted by shruti on 08/26/03 at 4:22 AM:
The MOV should be selected such that it is rated voltage is 10% more than it's normal operating condition and you should find out how much energy it will be dissipating (this u can take it from the manufacturers datasheet). For common mode protection connect the selected MOV between the line & earth and neutral and earth For differential mode protection connect the selected MOV between the two lines.